When recalculating MAWP for continued use, what thickness is used?

Prepare for the API 570 Piping Inspector Test with comprehensive quizzes and detailed explanations for each question. Enhance your skills and knowledge to excel in your certification exam today!

Multiple Choice

When recalculating MAWP for continued use, what thickness is used?

Explanation:
When continuing service, the MAWP calculation must reflect the pipe wall that is actually left, not what it was designed to be or what it was originally. You start with the actual wall thickness measured at the most recent inspection, and you apply a conservative adjustment for future thinning. Specifically, you subtract twice the corrosion loss that is expected to occur before the next inspection from that measured thickness. This gives the thickness to use in the MAWP calculation, ensuring the pressure rating remains safe throughout the interval. For example, if the measured thickness is 0.50 in and you expect 0.05 in of corrosion before the next inspection, you would use 0.50 − 2×0.05 = 0.40 in in the MAWP calculation. Using nominal or original thickness would ignore actual thinning, and using just the thickness after corrosion allowance would not accurately reflect the current, in-service condition.

When continuing service, the MAWP calculation must reflect the pipe wall that is actually left, not what it was designed to be or what it was originally. You start with the actual wall thickness measured at the most recent inspection, and you apply a conservative adjustment for future thinning. Specifically, you subtract twice the corrosion loss that is expected to occur before the next inspection from that measured thickness. This gives the thickness to use in the MAWP calculation, ensuring the pressure rating remains safe throughout the interval.

For example, if the measured thickness is 0.50 in and you expect 0.05 in of corrosion before the next inspection, you would use 0.50 − 2×0.05 = 0.40 in in the MAWP calculation. Using nominal or original thickness would ignore actual thinning, and using just the thickness after corrosion allowance would not accurately reflect the current, in-service condition.

Subscribe

Get the latest from Examzify

You can unsubscribe at any time. Read our privacy policy